the first cleaning be scheduled 1.006 years after installation
Explanation:
Given the data in the question;
U[tex]_{clean[/tex] = 300 W/m².K
first we determine the heat coefficient of the dirt surface;
overall heat transfer coefficient is reduced from its initial value by 25%
U[tex]_{dirt[/tex] = ( 1 - 25%) × U[tex]_{clean[/tex]
U[tex]_{dirt[/tex] = ( 1 - 0.25) × 300
U[tex]_{dirt[/tex] = 0.75 × 300
U[tex]_{dirt[/tex] = 225 W/m².K
next we find the inner fouling factor
[tex]R"_{f ,i[/tex] = [tex]a_it[/tex]
[tex]R"_{f ,o[/tex] = (2.5 × 10⁻¹¹)t
for the outer fouling water;
[tex]R"_{f ,o[/tex] = [tex]a_ot[/tex]
[tex]R"_{f ,o[/tex] = ( 1.0 × 10⁻¹¹ )t
now, we determine the total heat transfer coefficient
[tex]\frac{1}{U}[/tex] = [tex]R"_{f ,i[/tex] + [tex]R"_{f ,o[/tex]
we substitute
[tex]\frac{1}{U}[/tex] = (3.5 × 10⁻¹¹)t
so the first cleaning duration after insulation will be;
[tex]\frac{1}{U} = \frac{1}{U_{dirt}} - \frac{1}{U{clean}}[/tex]
we substitute
(3.5 × 10⁻¹¹)t = [tex]\frac{1}{225} - \frac{1}{300}[/tex]
(3.5 × 10⁻¹¹)t = 0.001111
t = 0.001111 / (3.5 × 10⁻¹¹)
t = 31742857.142857 seconds
t = 31742857.142857 / 3.154 × 10⁷
t = 1.006 years
Therefore, the first cleaning be scheduled 1.006 years after installation
Thank you for participating in our discussion. We value every contribution. Keep sharing knowledge and helping others find the answers they need. Let's create a dynamic and informative learning environment together. Find clear and concise answers at IDNLearn.com. Thanks for stopping by, and come back for more dependable solutions.